Help ET200X Siemens

Join Date
May 2002
Location
Varese, Italy
Posts
23
I have a problem with Siemens CPU 315-2DP with 2 ET200X conected, when I go in stop and next in Run on PLC on ET200 and PLC there is the led Bus Fault ON, to resume I must shunt down power supply.

Someone has a solution for this problem?

Thanks for Help
 
Siemens

Do you have expansion i/o via profibus? If so chances are one of those
modules has failed. Describe complete system and maybe we can help.
 
Luca,

You have probably already checked, but:

1 - Make sure your hardware profibus addresses agree with the addresses in your hardware configuration.

2 - Check your wiring (red to red, green to green) :)

3 - Make sure you have terminating resistors on both ends of the profibus network.

Good Luck -
Kevin Hammond
 