And if anyone's still listening from 2004, I did a project last week with the QTS "AN-X" gateway device for GEnius bus.
The client had three GE 90-30 controllers (SBA 16, 17, 18) exchanging global data on the GEnius bus. No I/O or drives or 90-70 controllers.
We attached the AN-X to the network as SBA 19, read the knowledgebase document about Global Data, downloaded two CSV files for configuration, and whammo, the data was in ControlLogix.
The AN-X also will represent the Global Data as a PLC-5 style Integer array, so you can send messages from a PLC-5 or SLC-5/05 to read and write the Global Data being exchanged with the GE controllers.
There are certainly other methods, including Prosoft modules in the SLC chassis, but we chose this because we already had the GEnius LAN running.