Hello all,
I need help understanding the logic concept behind this the attached file. I’ve been at it for about an hour, going on for about 21 hours without sleep starting up a new system, I think my brain is falling asleep here.

Anyways this is for a load hopper with an screw conveyor that unloads a given weight, I think N7:9 is the preset weight to be unladed from the HMI, but I don’t have a exact description.
What bothers me is the value in N7:10 it just does not calculate. I:15.2 is a analog signal from the weight system.
Any help greatly appreciated.
 
The SUB instruction on rung 2 is initiated by a 1-shot, meaning it will only execute ONCE each time 'Run forward' changes from OFF to ON.

🍻

-Eric
 
Assuming N7:10 is not written-to somewhere else, the calculation is a one-shot-rising which means if the values in either N7:8 or N7:9 change (and there is no reason to think they can't or haven't) no calculation will be done unit the next OSR trigger.

Looks like Eric got to it first....
 
To follow up, I think it works something like this:

When the system is started, it calculates how much to unload (N7:10) by subtracting the desired amount (N7:9) from the current scaled value (N7:8). This is only done at the start of the process (hence the one-shot). The value in N7:10 will not change until restarted.

The 'How Much to Unload' value (N7:10) is constantly subtracted from the current scaled value (N7:8) to determine how much has been unloaded.

The additional subtraction of 20 might be a 'tare' weight, or maybe to prevent emptying completely? In any case, the result goes in N7:68

Once completely unloaded (N7:68 greater than or equal to zero in rung 0), the system shuts off.

Of course, I could be wrong... ;)

🍻

-Eric
 

Similar Topics

Hi I have a machine which has recipes in the plc ,using indirect addressing, we have a screen where we enter the recipes and then save the recipe...
Replies
23
Views
4,184
Hi guys I have a machine that works fine, but today we had an issue where the operator speeds the line up to 20cpm the feeder but didnt adjust...
Replies
11
Views
3,209
Is there a way to do a mass copy of comments and tag names from one program to another? They are 100% identical, one goes online (uploaded from...
Replies
1
Views
3,179
I was trying to modify a program online the other day using RSLogix 500 . The PLC is a SLC5/05. I was online with the PLC, and could change...
Replies
2
Views
5,505
I had an idea to improve some of my standard programs, and make them easier to modify/expand in the future. Is there a way to address the current...
Replies
9
Views
3,698
Back
Top Bottom