modbus rtu whit siemens s7-318

hi

I have a profibus gateway connected to my plc s7 318

http://www.hardwarept.co.uk/product...nectivity/3/data-gateways/22/drl-dps-srm/187/

and I would like to know what kind of function block do I need to comunicate via modbus rtu I can not finde any information about what program block do I need.

this plc bill be the master in the modbus network

Hello;
Sorry, but the S7 will be a master on Profibus-DP.
The gateway will act as a Modbus Master.
The only thing that a DP master will see is the DP-slave interface of the gateway, and as such, you can access the data from the DP-slave directly on PIWxxx and PQWxxx addresses, or using SFC 14 and SFC 15 when you want to write or read a block of data to/from the slave.
The gateway configurator will establish the link between the Profibus data of the DP slave and the Modbus addresses that the Modbus master will exchange with the Modbus slaves.
Hope this helps,
Daniel Chartier
 

Similar Topics

Dear All, i am trying to connect Danfoss inverter with s7 200 cpu 226.but microwin shows following error at DATA Ptr.i assigned different VB...
Replies
1
Views
46
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
7
Views
221
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
Replies
6
Views
253
Hi, I'm having an issue with a mircologix not transmitting out. The current setup is a mircologix 1400 connected to a Guardian 100 Radio...
Replies
1
Views
109
If a device has Modbus RTU over serial and Modbus RTO over TCP and Modbus TCP then there is a difference between Modbus RTU over TCP vs Modbus TCP...
Replies
7
Views
479
Back
Top Bottom