1746-NI4 not working

Majortom2013

Member
Join Date
Jun 2013
Location
Mansfield
Posts
2
I have a 7 -slot rack with SLC5/05 1747-L552 Processor.
I have configured the inputs on slot 3 as I:3.0 I:3.1 I3:2 I3.3 and have tried different methods MOV COP SCP SCL to push the data into the N7 registers i.e. N7:30 etc the analogs work to the I:3.0 registers but will not move to the N7s?
Any ideas???
 
quick guess ...

you've put the new instructions into a new ladder file - and you forgot to include a JSR in the old ladder file ... therefore the new instructions aren't being scanned/executed ...

another way of saying the same thing: the new ladder file isn't being "called" into action ...

like I said, this is just a quick guess - but it's a very common problem ...

if this doesn't help, consider posting your entire RSS file ... you'll have to zip it first (forum rule) ...

and welcome to the forum ...
 
Last edited:

Similar Topics

Hello all. I have a 1746-NI4/B and I would like to get a cheap temerature module which I could use. I have found this on ebay...
Replies
9
Views
2,604
Is it really 0V input? You actually have a signal source hooked up to the input terminals? What does it read if you short the input terminals? Is...
Replies
9
Views
3,038
G'day lads, We are using an Allen Bradley PLC slc5/03 with an analog input module 1746 ni4. we have a sensor with a response rate of 250ms. in...
Replies
3
Views
3,136
I've already found the error and now this problem is solved. But I read about the RSlogix 500 and there was something like convert to BCD (Tod) a...
Replies
1
Views
1,799
I would be very grateful if someone could give me some guidance with a problem i have. I am trying to swap a 1746-NI8 which had failed for a...
Replies
8
Views
4,475
Back
Top Bottom