Or are you keeping the old 315-2DP, and need to hook it up with another new PLC that forwards the information to the new Citect ?
Yes - there is some control to the 315-2DP from Citect as well.
The new 'master' PLC is a dual processor, dual power supply, redundant type. It has remote I/O and Modbus RTU comms as well. It is networked with 10 other PLCs and they all have remote I/O and multiple Modbus RTU comms as well. The new 'master' PLC is to communicate with the 315-2DP.
The new Citect communicates with the new 'master' PLC which also acts as a data gatherer/concentrator for the Citect - a server PLC may be a better description.
The new 'master' PLC also controls the operation of the whole power station with the exception of the motor gen set which is controlled by the 315-2DP PLC.
Each generator has it's own PLC controlled by the master PLC via the two station master PLCs..
Each power station has a station master PLC as well to look after the 4 generators in each side.
There is a great deal of redundancy in the system as it is a critical site.
If there is a failure of a generator PLC/control system/generator then only that generator will be lost.
If there is a failure of a station master PLC then only that particular station of 4 generators will be lost in automatic mode but the generators will be available in manual mode for full synchronisation/load sharing.
It is quite complex and has been a joy to design and implement so far. Much of the testing/commissioning has been done at night or in short windows of a few hours when NASA have organised a world wide blackout for the three telescope sites as they all operate together most of the time so that they are all on or all off.
Hope this clarifies things.