Hi Guys!
I'm having real difficuly connecting a Lem current transducer (AT 100 B420) to a ET200s Analog module (6ES7 134-4GD00-0AB0).

I've tested the analog module with a 4-20ma generator all ok. And I've wired my meter in series with Lem when not connected to the analog mdule and get 4ma. But when I connect the two together I get nothing?
I've tried wiring the Lem directly to the analog module and in a powered loop but get nothing either way :eek:(

Am I missing something, it's been a while since I've messed around with this stuff.

Thanks

Roger
 
The DK 100 B240 is a 4 wire device, requiring a 24Vdc power supply.

Presumably, if you checked its output and got 4mA, then there's a power supply connected to the CT.

When you checked the output of the CT with a meter in series with the output, was the meter battery powered (hence, floating)?

If the power supply is grounded and your analog input is 'single ended' then the AI's (-) is grounded, and a ground loop can develop between the AI ground and the power supply ground. A ground loop can drive the signal off scale.

Is the power supply floating?
 
Last edited:
The way I interpret the ET200S block diagram is that this analog input module is designed to power 2 wire, loop powered devices with its own module's loop power.

2dw6nmd.jpg


The block diagram shows DC power, P1 or L+ (over on the left side) connected to terminals 1/3/5/7 which would wire to the CT's positive terminal, providing DC power to the CT. The CT's negative terminal wires back to ET200S terminals 2/4/6/8. The load resistor for the analog input is internal to the module with connections from each side of the load resistor running to the ADU.

The AT 100 B420 manual shows the typical wiring circuit for a 2 wire loop powered device, with an external power supply. But since the ET200S provides DC power, you should use an external power supply with this analog input module
 
Last edited:
The AT 100 B420 manual shows the typical wiring circuit for a 2 wire loop powered device, with an external power supply. But since the ET200S provides DC power, you should use an external power supply with this analog input module

I had tried using the ET200s dc power and an external power supply but got no joy. Do you think the issue is down to using a floating supply as you suggested in your first post?
I'm at home now but will try grounding the supply when I get back to work on Monday.

Thanks again

Roger
 
Sorry, I can't proof my own writing.

My last statement should have been, "But since the ET200S provides DC power, you should NOT use an external power supply with this analog input module.

Since the module sources DC power, you do not want to use an external power supply.

Just connect the CT's (+) to an odd numbered ET200S terminal, and connect the CT's (-) to an adjacent even numbered terminal.
 
Just connect the CT's (+) to an odd numbered ET200S terminal, and connect the CT's (-) to an adjacent even numbered terminal.

Tried doing that and it goes into overflow range.
I've also now linked my 0V to earth and still get the same issue.

Thanks

Roger
 
Do any of the inputs on this card function properly? I suspect that an external 24Vdc in the loop might have fried the card.

Does the card still 'see' your 4-20mA simulator in 2 wire mode?

Take the ground off. Grounds can be an issue with AI's.
 
Last edited:
Do any of the inputs on this card function properly? I suspect that an external 24Vdc in the loop might have fried the card.

Does the card still 'see' your 4-20mA simulator in 2 wire mode?

Take the ground off. Grounds can be an issue with AI's.

Sorted! Whilst re-checking the inputs with the simulator I noticed something. When I put 4.000mA on the input i get an overflow value, however when I put 4.001mA it works!
According to the manual I should have had a different value for underflow? I don't care anymore spent enough time on this.

Thanks for all the help!
 

Similar Topics

I'm having a little issue with an analog output. I've setup the channels as a 4-20mA output in the hardware config, and I've checked that the...
Replies
2
Views
4,668
Good afternoon, I am currently working with an HMI/PLC LP-a070 and I require at least one analog output, but the PLC does not have one. I was...
Replies
5
Views
56
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
Replies
5
Views
105
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
Replies
30
Views
1,111
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
10
Views
252
Back
Top Bottom