Wincc Scada configuration in Simatic Manager

recycled_mind

Member
Join Date
May 2007
Location
Cebu, Philippines
Posts
118
Dear Experts,
I'm very good in WinCC Flex but first time configuring wincc scada in simatic manager. My question is how to configure Wincc Scada in TIA way? I mean inserting OS in the simatic manager.
I have configure CPU314C-2DP as the PLC. I want to creat scada using WINCC SCADA V7.0 SP3. First, I add PLC-CPU314C-2DP, then add Simatic PC station, under simatic pc station configurations, i add cp5512 and a Wincc Application. This time, I doubt what's the next step in order to create connection between my OS (wincc scada) and the CPU314c-2dp. Please help.

thanks,
Alex
 
in device configuration add pc station and then add communication module for preferable connecion (if you would opt for profibus module = cpxxxx card in you pc). here is how i connect it (i used ethernet)

tia.jpg
 
in device configuration add pc station and then add communication module for preferable connecion (if you would opt for profibus module = cpxxxx card in you pc). here is how i connect it (i used ethernet)
Im not using TIA Portal, Im using Simatic Manager.
attachment.php

attachment.php

attachment.php

attachment.php



My question is, Is my simatic manager configuration correct? I just Insert OS on the simatic Manager. On the Path to target computer, what should I put?
Do i need to download the OS to PLC? On the OS2, Is my connection parameters correct?

Wincc Scada V7.0 sp3.jpg OS -Object properties.jpg Wincc Scada V7.0 sp3 OS download.jpg
 
Last edited:
You have to select the entry point inside WinCC for the WinCC conection to use PLCSIM. I don't have my WinCC with me at the moment, but i'm sure its on the TCPIP conection dialog (i am assuming your using TCPIP)when you right click on this select the "Unit"tab and select PLCSIM. When i get my WinCC i will post a screen shot.

Edit. Siemens info.

WinCC to PLCSIM
 
Last edited:
You have to select the entry point inside WinCC for the WinCC conection to use PLCSIM. I don't have my WinCC with me at the moment, but i'm sure its on the TCPIP conection dialog (i am assuming your using TCPIP)when you right click on this select the "Unit"tab and select PLCSIM. When i get my WinCC i will post a screen shot.

Edit. Siemens info.

WinCC to PLCSIM

Thank you so much, this solves my connection problems.
I already got the communication of my OS to the PLC.
On the Tag Management of any connection, you must configure first what type of connection you have for your OS to your PLC.
attachment.php


Tag Management system parameter settings.jpg
 

Similar Topics

Is it possible to connect a PC with running WinCC Advanced or Unified to a siemens PLC such as S7-1200 across different subnets? The computers can...
Replies
0
Views
85
We are using wincc scada WinCC system software V7.5 SP2 , connected to few plc . Past 3 weeks we getting this alarm continously when we checked...
Replies
0
Views
79
when i tried to go online, why its showing lie this
Replies
1
Views
87
I am utilizing both HMI and SCADA for my project. Both HMI and SCADA have identical tags. When I modify the tag value on HMI, it is reflected in...
Replies
2
Views
146
Got a new project using WinCC SCADA (V7.5 SP2) - the PLC is an ET200-SP, I've never had to communicate with one of these before (done plenty of...
Replies
3
Views
2,392
Back
Top Bottom