Here's my situation:
We have two PLC's exchanging produced and consumed tags.
We would like to change these to messages rather than just broadcast tags across a plant wide network. All of our other machines use messages.

Before I go making wholesale changes I'd like to identify all of the produced and consumed tags on these PLC's.
I've tried sorting through the tag list but I still can't see a way to sort out which are the produced and consumed tags?

Any ideas?
 
Ha! Something I know, for once...

Go to the Logic tab, and look for Produced tags. This will give you a list of the tags that are Multi-cast (as in, transmitted, similar to broadcast) by THAT program. It DOES NOT tell you which Multicast-ed INCOMING tags (from other processor(s)), are expected by THIS program on the link.

The original programmer may have been nice enough to tag/comment as such (it could happen).

These packets are on transmitted on an IP address other than the official IP address of the processor.

If you get a copy of WireShark (free IT application), you can sniff the traffic to verify. You will need a managed-type switch to do packet sniffing.

A Low end managed switch (Linksys/Cisco < $200) will also allow you to corral these noisy packets to the sub-segment of your network running these PLCs (running here as we speak). It may be easier than re-writing your entire program, especially if there are more than 2 PLCs involved. You would otherwise need an explicit message for each tag or tag group for each connection. It ramps exponentially. Normal traffic (programming, SCADA, etc. ) passes transparently.

Rockwell Tech support has not been helpful in these matters.

L8R

/DW
 
Depends on what version of RSLogix5000 you are running.

In Vers. 20 : above the tags window, use the drop-dowm menu in the "Show" box, choose "Configure", then in the "Filter On" drop-down in the Tag Filter dialog choose "Produced" and "Consumed" to see those tags only.

Previous versions were similar....
 
As luck would have it, I'm using version 20 :nodi:

Thanks for the tip Daba, I never realized I could search for them that way. Made my life much easier :whistle:
 
As luck would have it, I'm using version 20 :nodi:

Thanks for the tip Daba, I never realized I could search for them that way. Made my life much easier :whistle:

No problem....

I'm curious as to why you need/want to replace the Prod/Cons tags with messaging..?

And please remember that your filtering is persistant, so always check the tag "Show" properties when you can't see a tag in the database that you know is there. I generally clear the filters after i've used them, but i've been (temporarily) caught out a few times... embarrassing when teaching this stuff :oops:
 

Similar Topics

Hello everyone, I have an RSLogix5000 project which is running live in the factory but I need to make some changes to the logic. I want to test...
Replies
0
Views
1,098
Good Morning Everyone, I'm looking to use the GSV instruction to get I/O fault codes for my project so I know if there's a comms issue in my E/IP...
Replies
5
Views
821
The machine is running production. When trying to go online with the laptop the whole machine looses communication and faults out. Drives, HMI...
Replies
13
Views
1,877
Hello, is it possible to create a data block, something like shared datablock in Siemens STEP 7, in the RS Logix5000 PLC project? I would like...
Replies
3
Views
1,049
Hi all. This is a machine programmed by the manufacturer. There is an event task and the event tag is a MOTION_GROUP tag. Screenshot . Since the...
Replies
2
Views
979
Back
Top Bottom