problem with Omron CS1G

sylwek

Member
Join Date
Feb 2004
Location
Poland
Posts
26
hello,

I'm trying add a new module to Omron PLC CS1G.
I put this new module physically to the PLC.
In The cx-programmer I put in the "I / O Table" this new module and sent the new I / O table to the PLC.
And everything is fine until you turn off and turn on the power supply of the PLC.
After restarting power supply of the the PLC, in the PLC is error light, and when I read the I / O table from the PLC, then there's an empty slot for this new module. PLC loses a new I / O configuration after power supply restart. Maybe the old I/O table is is then read from EPROM?
CPU is CS1G-CPU43H (with EPROM card HMC-EF172).
The new module is CS1W-SPU01-V2.
 
You may be correct.
Check Dip Switch #2. If it is ON, the program is being transferred from the Memory Card at Power up.

Turning Dip Switch #2 OFF will prevent the Memory Card program from loading.

Hope this will help.
 
Rather than send the I/O table to the PLC generate it in the PLC and upload it - you should be good then. I always do it that way and let the PLC do the generation and have never had a problem.
 

Similar Topics

I have an Omron CQM1H-CPU21 and a NS8-TV00B-V1, I have followed the manufacturer's spec on how to set this up and all I got is the HMI is trying...
Replies
7
Views
869
Hello. I have a problem with omron sysmac cp1e controller delayed start. The controller has been working on the punch press since 2016. Recently...
Replies
1
Views
755
I have a Omron CP1L PLC that I'm having problems communicating with a NS5-SQ11B-V2 Omron HMI through ethernet . I have the exact same set up on...
Replies
3
Views
2,076
Hello, omron nt620c cannot access the system menu. After loading the system program and initializing, the message "No direct information is set...
Replies
3
Views
1,554
Hi! I am having a problem with the C200HE. It has a SRM21-V1 communication module with SRT1-ID08 remote input module. I think the protocol used...
Replies
1
Views
1,651
Back
Top Bottom