cip connection and MSG connection

b_e33

Member
Join Date
Mar 2013
Location
lolo
Posts
59
i want to comunicate between 2 PLcs so i want to use MSG instructions
i understand that ther is a limit, so if my controlLogix limit to 128 CIP connection that means i can activate together only 128 MSG instructions?
 
Based on my reading:

The limit on CIP connections are for persistent connections such Produce or Consume tags. The limit of CIP connections depends on the type of communications card (EN2T supports 256, ENBT supports 128)

So you can only have that limit of CIP connections active at the same time.

A MSG instruction can be programmed to be "one time only."
You can also choose to cache the connection (as a CIP connection) and you can leave it open, which would count toward your CIP limit.

That said, you can certainly have more than 128 or 256 MSG instructions as long as they all aren't executing at once, or you have too many cached connections.

Ken can probably shed more light on this than I.


I recommend reading these, they can probably answer most of your questions.

http://literature.rockwellautomation.com/idc/groups/literature/documents/pm/1756-pm012_-en-p.pdf

http://literature.rockwellautomation.com/idc/groups/literature/documents/rm/1756-rm094_-en-p.pdf
 
b_e33 has been shotgunning the Forum this morning with questions about maximum connections and simultaneous messages, and I'm not going to answer every thread he starts. My answers typically take me 20 to 100 times longer than his questions take him, and I'm out of resources.

My advice is to get the communications working between his two controllers before starting to worry about how to handle hundreds of MSG instructions.
 

Similar Topics

Hello Experts, I would like to ask a general question and just wondering if someone can help me to explain it. So I have a AB Compact logix...
Replies
9
Views
5,552
Environment: MMI Side: Intouch 10, ABCIP.5 connects with one 1756-L71; ABTCP.1 connect with few PLC5 1785-40E PLC side : 1756-L71 5570 Controller...
Replies
6
Views
2,330
We have a small ring network of point IO racks all using the 1734-AENTR communications adapter. These all are connected to a 1769-L33ER...
Replies
1
Views
2,975
Guys, Would you please let me know what the meaning of CIP connection is? For instance, when we say a controller has x amount of CIP connections...
Replies
16
Views
10,120
Hey folks, Just yesterday I upgraded and old L1 processor and its ENBT module with a new L71 20.015 and EN2T 10.00?. The L1 was used for nothing...
Replies
7
Views
4,876
Back
Top Bottom