Hey,

I have pump running off a vfd that controls level in a tank.
Now the client wants to have a progressive low flow setpoint meaning the low flow set points should about 10% of what the current flow is.
I have the logic working good for when the pump flow climbs by having the current flow in a limit block and if the current flow is in between the hi and low limits it takes 10% of the current flow and puts that into the low flow alarm setpoint.If the flow goes above a certain value it unlatches the first alarm sequence logic i just mentioned above and latches the next sequence but with a higher flow rate and limits.
Now how do I go about this when the vfd slows down?

Thanks
 
how about just always setting your low flow based on 10% less than the command vfd speed output?
 

Similar Topics

Hi guys , I know there is so many was to program plc, I'm after the best way to stop an output double triggering, I was working on a machine last...
Replies
7
Views
2,055
Hello everyone, Please forgive my ignorance, but I am new to the field of PLC programming. I would like to know if RSLogix 500 could be used to...
Replies
6
Views
10,854
Rockwell Allen Bradley Programming Software, RSLogix 5, RSLogix 500, RS Linx, RSLogix 5000, version 2007, 1 DVD ----------------------- The old...
Replies
21
Views
86,220
Please help to find the documents for programming RSLogix 500 for AB/SLC 500 on the net. I am new in this product so any information will be big...
Replies
4
Views
9,821
Hi, I'm writing a program Yokogawa PLC. Due to the, Yokogawa software is not able to do stimulation, thus I'm writing the program using RSLogix...
Replies
2
Views
7,674
Back
Top Bottom