sparkytex
Lifetime Supporting Member
Hello again! so the PLC I programmed was installed and tested and ready to run the chiller. The rep from Johnson Controls came up and discovered that our engineer made a mistake on the valve and control specifications. What Johnson wanted was a pneumatic modulating valve and a PID controller set up with the process variable as water inlet temperature and the setpoint at 18 degrees ( which I was told originally was. What was installed was a 3 way solenoid valve that actuates open when the temperature was 13 degrees or lower and a bypass pump was then started to bypass the chiller, ( water is already cold enough, does not need chilling ) and above 13 degrees the valve actuates closed and water runs straight in the chiller and the bypass pump is not running. So its too late to change out the valve and there is a way to make this valve work properly without constantly actuating around 18 ( i.e. water temp floating around 17-19 degrees ). I was told I could put in a deadband so that when the water temp reaches 18 degrees and climbing the valve will actuate closed, not just right at 18 degrees, and vice versa when the water temp reaches 18 degrees and dropping the valve will actuate open not just at 18 degrees. How do I go about adding this "deadband" into my ladder logic. I will load up my existing program on the site under downloads. please help as the rep is on site today and would like to see this thing run!! thanks