Power Supply wiring of Modicon M340 BMX AMI 0810

TahirQ

Member
Join Date
May 2013
Location
Riyadh
Posts
54
Can Anybody please tell me about the power supply wiring of Modicon M340 BMX AMI 0810 module. All i can get from the catalogues is Two wire sensor wiring.No info about power supply wiring.
 
the module itself is powered from the backplane. you must wire the sensors so that they provide the 0-20mA or -10 to + 10V signal to the terminals of the AMI module. How this analog circuit is powered will depend on the specific sensor.
 
I have done wiring of Digital I/O Modules only. This is the first time I am using an Analog Input Module.The Standard power supply module CPS 2000/2010 only powers up the module not the channels. I am getting confused because of wiring diagram of Analog Input Module as there is no explanation about how to power up the channels.
 
You Will Need an external dc supply to power your loops.

what i normally do is use 3 terminals per Channel

TERM1 - Positive 24vdc
TERM2 - Positive Signal
TERM3 - 0vdc coupled with negative signal.

then for loop powered instruments you connect to terminal 1 and 2 and for instruments with their own supply's you connect to terminal 2 and 3.

hope this helps
 
Without allowing for circuit breakers or fuses it should look something like this. Assuming you are measuring 4-20mA like chud mentioned.

diagram.jpg
 
Last edited:
Does Anybody how M340 interprets 4-20 mA current signal. In the form of Integers or Does it convert the current signal to BCD? I need this info for scaling analog input
 
Not sure but think its integers. But why do you need to know this? If you assign an integer to the channel you get int value. And scaling can be done on the cards configuration directly
 

Similar Topics

I
Hi, does anyone know what a wiring diagram of a 240V power supply to a plc and pump looks like?
Replies
48
Views
19,339
DaMan
D
I am looking for power supply that I can mount on vertical DIN rail, and when mount that way is =< 4" wide. this is what I have now.... this is...
Replies
21
Views
497
I have Rhino 120 to 24 dc power supply and it has 2 Positive and 2 negative terminals on the DC side but no ground terminal. Should I connect one...
Replies
9
Views
385
We've still got a ton a PLC 5's installed and running. We lost a 1771-P7 Series B power supply. There are a lot of 1771-P7 series D power...
Replies
3
Views
205
Long ago, it was often a customer spec to always use a transformer for isolation of the control circuit from the rest of the equipment. For 24vdc...
Replies
5
Views
628