Micrologix1200 Communication.....

JoseM

Member
Join Date
Jul 2011
Location
Texas
Posts
381
Can I communicate to a Micrologix 1200, going through a Panelview C600?

I have this machine made by SIDEL that has a Micrologix 1200 talking to a Panelview C600 via RS232. I want to access the PLC program on the Micrologix because I have to make a small Modification.
 
I don't think that the RSLinx Enterprise drivers inside the PanelView Component will allow you to perform channel-to-channel browsing.

The easiest thing would be to unplug the PanelView from the MicroLogix 1200 controller and press the DCOMM button on the MicroLogix to set the communication channel to the default DF1 Full Duplex settings. Press it again to set the communications channel back to its programmed settings.

Remember that the MicroLogix 1200 does not support online editing; no matter what you do, you'll have to put it in Program mode to download the modified program.
 
what model of 1200 do you have? some have 2 com ports and some don't. If yours doesn't then you'll have to disconnect the panelview to program the plc.
 
10-4 Ken. I guess I have to wait until the machine goes down to do the modification to the PLC code. I was looking at an offline copy of the program running on the Micrologix 1200 and channel 0 is set for "DF1 Full Duplex".

Do I still need to press the DCOMM key to get it to communicate with RSLinx?

That one Micrologix only has one port and its used for the HMI.
 
Its likely that the MicroLogix is still in DF1 Full Duplex mode with the default settings. Pressing the DCOMM button will probably not be necessary.

Max is correct, of course, that there is a "1200R" version of the MicroLogix with a dedicated HMI serial port, for exactly this sort of situation where you want to monitor the controller without disconnecting the HMI device.
 

Similar Topics

I have Micrologix1200, can I communicate it with 1747-PIC/AIC +Driver. This unit is being used with HMI. I have RS LOGIX500 software installed...
Replies
4
Views
1,985
Can Anybody Help Me????? My problem is I need to know the pin out of a comms lead so that I can communicate to a Micrologix 1200 via an AIC+...
Replies
2
Views
1,628
Hello let me explain my problem. I just got tossed into a somewhat complicated job because the person that normally does the writing is on...
Replies
5
Views
3,827
I have a micrologix 1200 that will run one of three different timing sequence, depending on which input is triggered. I'm trying to find the best...
Replies
6
Views
3,454
How to check the communication between the Micrologix1200 to Citect SCADA. I use PLX51-DF1-ENI router to communicate in scada. I tried to use...
Replies
0
Views
1,344
Back
Top Bottom