Hello all,
Thanks in advance,
I am trying to understand my position here a bit better. I am more acclimated to logix 5000.

In auto I have an internal/external setpoint operating on a pid loop with a flow meter. When an h/o/a switch is toggled to manual I want the PID ignored and the the setpoint will be just a 0-100% speed for motor.

I want to move that scaled value into the analog out to the drive for instance o:1/0.

It tells me I must address this at the word level. I'm used to being able to move that value directly to the source....so to speak. I guess I don't understand if I cant move a value into the output, how do I go about having that output reference it at the word level?

Excuse my ignorance, still new to this.

Thanks
 
O:1/0 is a bit level address (the "slash" always denotes a bit).
If your target analog output is Channel 0 of the Analog Output module installed in Slot 1 of the 1746 chassis than MOV your value at Destination O:1.0
 

Similar Topics

Can someone explain to me the purpose of this IOM instruction? N10:8 is fed from a PID and as you can see, when the PID Control bit is enabled...
Replies
2
Views
1,398
So I used the migration tool for converting RSlogix 500 to Studio 5000 and the resulting came out. See attached png files. I am having trouble...
Replies
10
Views
3,676
I've attached pics, below. I'm in the field right now an am trying to communicate to the Micrologix 1500 through the 1761-NET-AIC (Ugh!) to...
Replies
6
Views
1,935
Dear friends, i wand to creat a program in which my motor runs 6 month in every year. Means motor on 6 months and ofer...
Replies
12
Views
4,500
Hi guru's I'm after you help , I'm looking to capture data changes on a Hmi (pvp) I would like to know the best way to tackle this ? I would like...
Replies
5
Views
2,326
Back
Top Bottom