I´m using PL7 Pro from Schneider
I use a FTON timer, whose output is %M20
Here is the deal, if %M20 is high when I start timing, it remains high although the timer hasn´t arrived to the preset value.
Has anyone had that problem??

Thanks in advance
 
aracioppi
FTON is a on_delay timer
It has a many parameter to difine it.One of them is the "EN" which means the enable input for this function .
As long as the enable input is on the timer counts up the time until the current value equal to the preset value .When this occur the output goes on.When the enable input goes off the output goes off directly regardless what is the current value in the timer.
it's imposible to start count when your output is on (%m20 in your case)because to start count "EN" goes from "0" to "1" and when "EN" equal "0" the output must be "0".
Please check for m20 may be you used it twice in the program.
i hope that could help you.
 

Similar Topics

im new guy here...i have problem about the connection between dc servo motor and plc...for ur information, my project is to control the speed of...
Replies
0
Views
3,282
Hey all, I am starting a new project for a customer and I am adding in solenoid valves. Once added, I noticed there was a lack of an Output...
Replies
0
Views
60
Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
Replies
4
Views
125
Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
Replies
1
Views
105
Hello! Hope you are great. I need to make a change in a PLC with ladder logic. I will mount a analog valve and I need to control it in ramp up...
Replies
7
Views
316
Back
Top Bottom