Hello,
I am wanting to get a Magelis to read holding registers from an IO device using FC04, but in testing it always seems to use FC03.
The manual says FC04 is a supplementary address, yet I need to use it.

I don't think the IO device supports FC03 for input registers, the example only shows output image for FC03.

I have used this IO type with a PLC using FC04 and m is it works, I just wanted to copy the same config.
For reference, I can set outputs from the Magelis using the same config as the PLC so know this is correct.

Any suggestions on how to use FC04, or to force it to read using this function?
 
Not sure, but a couple of things to check
if iec addressing mode is selected use addresses in the format %IW123 (dont remember seeing this option)
if iec mode is not selected use addresses in the format 30123
 
Not sure, but a couple of things to check
if iec addressing mode is selected use addresses in the format %IW123 (dont remember seeing this option)
if iec mode is not selected use addresses in the format 30123
Thanks Geoff, the IEC mode is only for Modbus/TCP, not RTU. I have tried both types of addressing 3xxxx & 4xxxx, but both seem to use FC03.

I have double checked the manual for the Remote IO, & there implementation of FC03 only supports reading of Output registers. 🔨
 
Geoff,
oops, the IEC mode is also available for RTU mode, I just overlooked where it was :(
Local support have advised of a solution that I am yet to test, I am hoping to do so later in week.
Interesting enough, when using Kingfisher Telemetry equipment, an address is only entered, so it uses FC04 by default as it always requires to read Input registers rather than holding registers.
 

Similar Topics

Hi, I want to connect a Schneider Magelis HMIS5T to a Danfoss FC102 via Modbus to display some values and just having some issues with the...
Replies
4
Views
3,420
Dear Experts, I am using XBTL1000 v3.5 to configure Magelis XBTF Terminal but cannot transfer application due to a missing modbbus protocol...
Replies
0
Views
1,388
We have a Magelis XBTGT6330 that we want to connect to Modbus Plus network. My question is: can we connect the XBTGT6330 directly to the Modbus...
Replies
0
Views
2,625
Hi, I want to connect 2 Twido ldmda20drt PLCs to a Magelis GT5330 Hmi through Modbus. Magelis is the master controller. Twidos have Rs-485 port...
Replies
10
Views
7,474
I have a SCADA system trying to poll 3 x Magelis XBTGT1335 HMI's using modbus TCPIP. The SCADA system is acting as the master. The problem is with...
Replies
4
Views
3,789
Back
Top Bottom