lbric
Member
hello
i am trying to setup a 4-20 analog input signal for a plc, i am using a jenco 77a type j thermocouple converter with a 4-20ma output (temperature range 32-532). for my zero input temperature, aprox 40 degrees, i am able to set the zero output value to 4ma. i read that the span should be the difference between the high and low range and in this case sould be 20-4=16ma,but when i try to set the span on the converter it max out at 6.3ma. my high temperature value is aprox 80 degrees. i want to feed this signal to a plc analog input to display temperature value on an hmi.
thanks
i am trying to setup a 4-20 analog input signal for a plc, i am using a jenco 77a type j thermocouple converter with a 4-20ma output (temperature range 32-532). for my zero input temperature, aprox 40 degrees, i am able to set the zero output value to 4ma. i read that the span should be the difference between the high and low range and in this case sould be 20-4=16ma,but when i try to set the span on the converter it max out at 6.3ma. my high temperature value is aprox 80 degrees. i want to feed this signal to a plc analog input to display temperature value on an hmi.