Dear,

in my company, we are using siemens plc Cpu 314-2dp.
One day we remove the two machines out of 10 from a single line. when we removed the line, the bus fault and signal fault appear. But the cpu is running and our line is also running.
Can we run the line forever with this cpu status or future something can be happend?

Our plc program is ok. CPU is ok and it is running but the signal fault and bus fault LED's flashing.
is it effect our program? or effect to cpu execution? can anyone help.
 
It's not right, but it will run

The Signal and Bus fault, lights on the PLC are configuration errors, because the config is looking for nodes and I/O that are now removed. You should be ok as long you have OB82,OB87,and OB122 in your program, which you must already have, or the plc would have stopped.
 
thanks alot for reply.
the program having OB's which you mentioned. My question is, this bus fault and signal fault will effect the program or not? and we can run the plc program as long as possible.
 
The suggestion, obviously, is to fix the hardware configuration : in the future you may not see further serious problems.

Anyway yes, your program can run.

The Bus processor is indipendent from the CPU, it refreshes the I/O bus, if something is wrong an error is reported to the CPU which calls the errors OBs if present; if they are missing it goes in stop mode.
 
One day we remove the two machines out of 10 from a single line. when we removed the line, the bus fault and signal fault appear. But the cpu is running and our line is also running.
Obviously you guys had no clue about what you were doing and are lucky it kept running...
and "SF" means system failure, not signal fault
 
well, if we're gonna push it, it's System Fault not System Failure :D :D
Well, since it's obvious they didn't have a clue about what they were doing, the difference between System Failure and System Fault, as big as it might be (or become), didn't bother them anyway o_O

Luckily for the OP ("original poster") the system didn't fail, it only had a fault, which was dealt with in the program. Hooray for the OP (meaning "original programmer" here)!

Kind regards,
 
You can use SFC12 to activate and de-activate nodes.

If you are temporarily removing nodes and don't want the red lights flashing, then maybe create blocks that call SFC12 for each node and a button to enable/disable the nodes.

When you remove a node, you could de-activate the node via the button, red light goes away, and when you put it back in re-activate it to re-enable faults.

It could also be done with a soft switch in the PLC, which maybe wiser.
 
SF Fault

Greetings sparkies,

In his case if a NODE is removed, and the CPU is running though the BF & SF LED's are lighting, the programmer must have programed OB86 as well.

Cheers
 

Similar Topics

Hey when I turn on my Siemens PLC CPU 216-2 after runing 10 minute it's stop and showing SF indication after I turn off and some time later turn...
Replies
0
Views
110
I was trying to communicate between Siemens ET200S IM-151-8 PN/DP CPU to Rockwell Allen Bradley L73 through Hilscher Gateway NT100-RE-EN. Using...
Replies
0
Views
105
I'll preface this by saying this is the first time I've worked on a Siemens system and I'm fairly unfamiliar with them. I might mess up some of...
Replies
29
Views
721
Has anyone come across this kind of problem: I have 1215FC cpu with profinet and profibus devices. Because of one device, I would have to...
Replies
10
Views
952
First of all, it's a pleasure to join this community, I already have a few years of exp in this sector but never registered on a plc forum, so...
Replies
4
Views
779
Back
Top Bottom