hiiii everyone

I am using cu 240-e 2pn control unit & IM 151-8 PN/DP cpu.Ethernet cable I am using is 6XV1850-0AH10.

Now my problem is
I am connecting P1 port of PLC to P1 port of first VFD.
P2 port of first VFD to P1 port of second VFD
Similarlly P2 port of second VFD to P1 port of third VFD
Like this I have connected 7 VFDs.
Now my doubt, Is the connection right?
OR I have to use ethernet switch.
 
Your using the G120 basically as a switch
So your ok
If you put your connections in the topology editor the p1 etc
Ports must be wired as the topology editor is configured
 
You should consider if it is possible that some part of the system is shutdown, but the rest of the system should still be able to operate.
If this is not the case, you can connect in any which way.
If it is the case, then you must make sure that something that needs to be able to operate isnt disconnected when something else is shutdown. You may have to cleverly design the order in which one device links to the next device. Or you may have to use a switch to distribute all connections.
 

Similar Topics

Hy, can we use shielded ethernet cables for drive-cliq connection to sinamics s120 components? Will any problems happen? I contacted siemens...
Replies
0
Views
4,249
Hy, can we use standard ethernet cables for drive-cliq connection to sinamics s120 components? Will any problems happen? Appreciate your help.
Replies
5
Views
5,791
Hello sameone have Beckhoff PLC Siemens Sinamics V90 configuration example?
Replies
0
Views
98
Hello, I use a Siemens Sinamics G120C inverter in combination with a S7-1200 cpu. I use the Main Setpoint with the Providrive option and send...
Replies
8
Views
721
Hello to all, I have a STEP 7 project (v5.6) with S7-400F CPU and Sinamics S120 drives with CU320x2PN (ord. nr. 6SL3 040-1MA01-0Axx). I need to...
Replies
7
Views
937
Back
Top Bottom