Hello all,

Where I work we have some proximty sensors wired to a S7 ET200 input card, for the plc to use and also display on SCADA, they now also want lamps next to these to show where the machine is (it can be in three positions with a sensor for each). The sensors and junction box for them are virtually next to where the lamps need to go, however the ET200 is a bit away and doesn't have any spare outputs so will n eed to extend or find a couple of other spares and run cables half way round the factory, can I just spur off the cable for the plc input to the lamp or will this cause a problem for the plc input?

Any help greatly appreciated.
 
Maybe wire the prox to switch a two pole relay. One pole firing the Plc input, with the other pole energizing the lamp. That way the two stay isolated.
 

Similar Topics

I am having a step7 v5.4 program where the blocks are encrypted and locked. And the manufacturer is stopped the support. Is there any ways to...
Replies
2
Views
176
Good Morning, Hoping someone with some Siemens experience can give me a hand with this one. Customer has a S7-200 cpu, which has a 6GK7...
Replies
0
Views
248
HI! HOW COULD I OBTAIN THE NAMES OF THE STEPS OF A ROUTINE IN SFC LANGUAGE IN STUDIO5000? Or is there a system variable that gives me those...
Replies
0
Views
339
I'm just trying to figure out the right method of adding a DO card to an existing rack. It's not the *next* open slot, but I have to move the AO...
Replies
5
Views
547
Hi Siemens Experts, I am hoping someone can shed some light on my issue. I have uploaded the code from a S7-300 (317-2PN/DP) using Step 7...
Replies
9
Views
673
Back
Top Bottom