James Mcquade said:
...what do you mean by sccr?...
...SCCR - short circuit conductor rating?...
...without any protection - its wide open.
it will carry current until it melts or is no longer conducting the neutral or ground. then it starts all over again when maintenance gets into the panel trying to figure out what happened. ONLY, this time, someone becomes the path to ground.
James, you're close on the SCCR part, but while explaining about having no fuse you have also outlined the effects of a SCCR being under-rated.
Short-Circuit Current Rating (SCCR), or Withstand Level, is the maximum level of short-circuit current (kA) that a component or entire assembly can withstand.
The SCCR must comply with NEC 110.10.
Not to be confused with...(not saying you are James)
The Interrupting Rating (IR) is the maximum current, at rated voltage, that an Over Current Protective Device (OPCD) can safely interrupt. The IR rating of the OCPD should be no less than the highest potential current at its line terminals.
The IR must comply with NEC 110.9.
To meet SCCR requirements, both a suitable IR and SCCR needs to be considered for protective devices.
msaeger said:
...The power supply is UL 508 rated...
James Mcquade said:
...it doesn't matter if the power supply is UL508A rated...
UL508 pertains to the industrial safety standards for individual components. (Circuit Breakers, disconnects, switch fuses, etc.)
UL508A pertains to the industrial safety standards for assemblies of components. (Industrial Control Panels, Machines, Systems, etc.)
James Mcquade said:
NFPA 79 states that new control panels shall not have control power over 120 volts.
James, the power supply is fed 2 phase 480V, the
control circuit is 24VDC here, so the 120V rule isn't being breached in this case.
The
PULS ML100.200 power supply is fused internally.
General Description said:
The ML100.200 is a simple and cost effective approach to convert the AC voltage of a typical three phase system into a regulated DC voltage. It only requires two phases and thereby saves terminal space, terminal cost, wires, fuses and installation time.
The ML100.200 is very compact, high efficient and easy to use. The input is internally protected, which makes external fuses unnecessary in many cases.
Internal input fuse T3A15.
That keeps NFPA\NEC happy as there is a suitable OCPD in front of the PULS power supply.
But what about the SCCR?
SCCR only applies to Power Circuit Components up to 600V. NEC 110.10 requires the SCCR to be adequate enough to protect the circuit equipment from sustained short-circuit currents, which may pose a potential electrical shock hazard or fire risk.
NEC 110.10 also requires the SCCR to prevent extensive damage to the equipment within acceptable limits or criteria. i.e. once the fault damage cannot pose the above risks outside of the panel enclosure. The acceptible limits can get tricky when the situation you mentioned occurs James, opening panels to find out where the smell is coming from?
A specific fuse or circuit breaker needs to be used to provide the necessary SCCR to withstand the maximum potential short-circuit current.
Fuses tend to be higher rated, usually 200kA, but it depends on the fuse type and potential fault current. If the fuse in the PULS power supply is a class CC, J, T, R or L UL248 branch circuit type fuse, then you can give it a 200kA SCCR. If not, I would rate it similar to a UL 489 Circuit Breaker at 5kA to be safe.
Is your disconnect fusible or non-fusible?
If fused with any of the above fuse types, it can give you up to 200kA SCCR.
If un-fused, then 10kA SCCR, but only if you use above fuse types on the branch circuit after the disconnect. Otherwise 5kA SCCR.
If you were to put current limiting fuses on the incoming feed, this would then reduce the potential short-circuit current. Reducing this would instantly increase the SCCR for the whole assembly i.e. the panel. This is beneficial in many ways, as SCCR is based on the weakest link principle. If the lowest rated component had an SCCR of 5kA, this determines the overall assembly SCCR. By decreasing the potential short-circuit current at the feeder, this could potentially bring the assembly SCCR up to 100kA.
Note: Control Circuit Components, typical <15Amps, do not need a Short-Circuit Current Rating.