we are using allen bradely AIC+ for connecting PLC SLC 05/03 to PLC, now i want to change 1761-NET-ENI in place of AIC+, so please tell me the procedure.
The 1761-NET-ENI runs only DF1 Full Duplex protocol on the serial port side, so the SLC-5/03 Channel 0 serial port must be configured for DF1 Full Duplex (the default configuration) to be connected to the 1761-NET-ENI.
The procedure for connecting and configuring the 1761-NET-ENI can be found in the 1761-NET-ENI User Manual.