monkey082506
Member
Hi all,
I am messing with an existing system that is operated with a PLC5-60. The system has remote I/O with the 1771-ASB module. The system use to have a rack that had a 1771-IXE thermocouple card in it. They recently wanted to upgrade that rack, so they bought some SLC cards/chasis/ASB module and replaced it.
I have the 1746-NT8 card in this rack and I can not for the life of me get correct readings from what the operators say was displaying. There is a temperature gauge on the outside of a freezer and when the freezer is at 46 F my reading on the NT8 is 46 F. However, when the value gets lower than about 20 F my temperature slowly stops being accurate. The value on the gauge will read about 11 F and my reading will be about 20, it could be -10 and I'll be getting a reading of +11.
I'm using 100 mV ICTDs for the inputs and the card is configured for the 100 mV signal. The 1771-IXE card that was in the old rack was configured for 2's compliment. Which from my understanding was returning a value of 0-8190. There was then a calculation of ((((x|24.9)-273)*9)|5)+32) to give the value in degree F.
I configured my 1746-NT8 card to receive 100mV signal and scale it at 0-16383. Then I did the exact calculation just divided it by 2 or 49.8 and carry on. However, something is not clicking.
Any insight on this would be more than helpful. It seems like something simple but I'm missing something and I'm beating my head against the wall.
I've attached the manuals for both if needed.
NT8: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1746-um022_-en-p.pdf
IXE: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1771-um658_-en-p.pdf
Thanks!
I am messing with an existing system that is operated with a PLC5-60. The system has remote I/O with the 1771-ASB module. The system use to have a rack that had a 1771-IXE thermocouple card in it. They recently wanted to upgrade that rack, so they bought some SLC cards/chasis/ASB module and replaced it.
I have the 1746-NT8 card in this rack and I can not for the life of me get correct readings from what the operators say was displaying. There is a temperature gauge on the outside of a freezer and when the freezer is at 46 F my reading on the NT8 is 46 F. However, when the value gets lower than about 20 F my temperature slowly stops being accurate. The value on the gauge will read about 11 F and my reading will be about 20, it could be -10 and I'll be getting a reading of +11.
I'm using 100 mV ICTDs for the inputs and the card is configured for the 100 mV signal. The 1771-IXE card that was in the old rack was configured for 2's compliment. Which from my understanding was returning a value of 0-8190. There was then a calculation of ((((x|24.9)-273)*9)|5)+32) to give the value in degree F.
I configured my 1746-NT8 card to receive 100mV signal and scale it at 0-16383. Then I did the exact calculation just divided it by 2 or 49.8 and carry on. However, something is not clicking.
Any insight on this would be more than helpful. It seems like something simple but I'm missing something and I'm beating my head against the wall.
I've attached the manuals for both if needed.
NT8: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1746-um022_-en-p.pdf
IXE: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1771-um658_-en-p.pdf
Thanks!