Looking for some help understanding the bias function on a PID insturction. Currently my PV is scaled to 0-4095 (level transmitter) with the PID engineering unit maximum 15 and engineering unit minimum -15 within the PID Insturction.

My setpoint is coming into the PID instruction is in engineering unit (SP = -.5).

Do I need to bring in my bias as a +/- 100%?

How does the bias have an effect on the Control Output?
 
The bias is added to the output. If you are controlling level the bias probably doesn't need to be used. If you are controlling level then you are usually controlling the flow in or flow out of a tank. If you have a flow measuring device you can use that to adjust the bias. For instance, if your pump pumps controls the outflow and it pumps 1 cubic meter per 10% output and you know the inflow is 1 cubic meter you could set the bias to 10% of its range so the output will be 10%. This way the pump can instantly respond to the changes in the inflow without waiting for an error to build up. If the level control is not that critical then don't bother.
 

Similar Topics

Hi, Long time not in the forum, and not in the programming. I´m getting back. I was issued a conversion from RSLogix 500 to RSLogix 5000 (studio...
Replies
0
Views
1,277
So I have a PID loop on an 1756-L61 running V17 software just for background. Also the PID PV is a pressure transmitter and the CV is speed sent...
Replies
1
Views
863
I have 3 valves that I need to open for 1 minute every 30 minutes, but not all at the same time. I have one TON timer (Start Blowdowns Timer)...
Replies
15
Views
4,583
Hi All, I have a PID control application that I would like to get your opinions on. As I am reality new to PID loops I am struggling somewhat...
Replies
14
Views
4,214
Hi, I am confuse with the scaling tab on the PID dialog box. On the Process variable I am using a tag that is already scale. 0 to 16 Feet Level...
Replies
2
Views
2,354
Back
Top Bottom