Analog Card Upgrade

antsrealm

Member
Join Date
Dec 2010
Location
Brisbane
Posts
207
Hi,

I have a project on at the moment that has a control logix processor 1756-L61 connected to a PLC 5 remote rack via a 1756-DHRIO.

Now in the PLC5 rack is a 1771-IFE Analog Input Card. We are upgrading the remote rack to a control logix rack and it will be using a 1756-IF6I card instead.

When I looked at the config of the 1771-IFE it was setup to use two's complementary as the data format. I was hoping to just move the input data from the new card into the register that was holding the input data from the old card.

Will the new data be the same as the 2's complement data assuming I have set the scaling the same??

Thanks,
Tony.
 
Unfortunately, the Legacy 1771-IFE Analog Input modules provide a 12-bit resolution while the 1756 family Analog Input modules carry a 16-bit one.
The only data format choices for the ControLogix Analog modules are Floating Point and Integer.
In your case, since the replaced and replacement module carry different resolutions, you will have to redo the scaling; in order to be able to scale a 1756 Analog module you will have to choose a Floating Point module data format.
Refer to Pages 49-50 of http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1756-um009_-en-p.pdf
vs.
Page 4-3 of
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1771-um663_-en-p.pdf
 

Similar Topics

Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
Replies
0
Views
87
Hi all, i was trying to learn the analog card and got pulled off. now i am asking for your help again. this is what i have. all i/o are enabled...
Replies
3
Views
1,304
Good Morning , I have a RTD , that I would like to wire into a 1756-IF8 Analog Input Card. Would you all a simple wiring diagram , of what...
Replies
4
Views
1,201
We have an omron CJ2M-CPU12 PLC that we are having issues with an AD04U analog card. it is connected to a K type thermocouple sensor. The card is...
Replies
4
Views
600
Hi all, While i am not new to omron, i'm totally new to the analog part and lost. i have a CJ2M cpu 33. then there are 4 i/o cards card 5 is a...
Replies
26
Views
2,579
Back