Checking fault codes and fixing

unsaint32

Member
Join Date
Oct 2012
Location
minneapolis
Posts
365
Another newbie question from me....

My MLX1400 threw the following error code: Major Halt S:1/13 and S:6 = 08h. As you can tell, I am a newbie to automation. I looked up the error code table (in RSLogix500's help file) and found the hex code 0008.

Q1) Is it the way I am supposed to diagnose the fault?

Q2) Also, in Controllogix 5000, is there way to look up the status file like MLX1400? Or is accessing fault codes totally different in CLX5K?


Thanks.

NEW-2.jpg NEW-4.jpg
 
A1 - Yes

A2 - Totally different in Logix5000 systems, there is no "Status" file that can be displayed on the programming software and read by/written to directly by your PLC code.

Everything is held in an object-orientated database called the "System Value" area.

Of course the programming software reads and writes to this area without you having to worry about the actual location of the data.

But if you want to interrogate stuff like fault codes, module status, etc., from within your code you have to use the instruction GSV (Get System Value), to read the system data into a usable tag, and if you need to write to the status area you use the SSV (Set System Value) instruction.

For a new user of Logix5000 it all looks unfamiliar and formidable, but it isn't that difficult once you've seen an example or two...
 
I did read about GSV and SVS on a Rockwell manual. I will try again. BTW, after I posted this question, I realized 1756 L71 has fault codes scroll by on the module screen. I guess I can look that code up. Is that a reliable starting point to handle faults? Or do most CLX5K users create GSV and SVS?
 

Similar Topics

Hi, lets say that wehave one S7-1500 and one ET200S connected through profibus. I remove profibus connection from ET and detect a problem using...
Replies
1
Views
1,995
Hello, can someone share/explain How to check comms between PC and PLC via TeamViewer? TIA
Replies
14
Views
426
Hello, I have a question on an OCR application I am doing. I am reading in 16 characters that come from a camera into the plc in its input words...
Replies
4
Views
1,291
I have some questions about MSG Type checking Does a MSG instruction care if the name of the UDT type are different on each PLC as long as...
Replies
6
Views
3,506
I just finished making my 3rd service call to a large machine shop, troubleshooting PLC issues. I can see that none of the PLC or HMI programs are...
Replies
11
Views
3,088