Hello. I am trying to calibrate a RTD module unit from RS logix 5000, and keep failing.
INFO:
PLC - Compact Logix 5370 L1 Series
HMI - Panel View Plus Compact
Ethernet - AENT/A Remote
RTD - 1738-IR2M12 (100 to 500 ohms)
Everything is connect thru ethernet connections.
I go online with the PLC and open the calibration tab from the RTD module in the I/O config tab in rslogix 5000. When I run calibration from the calibration tab, it starts fine. I connect the low source (100ohms) and click next...then I connect the high (500 ohms) and click next. It fails everytime I try. I dont get it.
Anyone out here have any experience here?
Thank you.
Matthew Sayers
INFO:
PLC - Compact Logix 5370 L1 Series
HMI - Panel View Plus Compact
Ethernet - AENT/A Remote
RTD - 1738-IR2M12 (100 to 500 ohms)
Everything is connect thru ethernet connections.
I go online with the PLC and open the calibration tab from the RTD module in the I/O config tab in rslogix 5000. When I run calibration from the calibration tab, it starts fine. I connect the low source (100ohms) and click next...then I connect the high (500 ohms) and click next. It fails everytime I try. I dont get it.