Trying to download the program--can't commect to it. Model2711-K6C9. Using a pass through cable & doing the auto config in Linx. Just won't set up I know the cables are good. I used a null modem cable and downloaded from the processor--changed to the pass through--tried to do the auto config-failed. Any help will be appreciated.
Panelview settings
max node 1
node 0
baud 19200

Thanks Terry
 
Last edited:
Your PV supports DH485 protocol.

The printer/aux port is configured for printer only, it cannot be changed on DH485 PV's.

So you are going to have to use the RS232 comm port configured for DH485 to upload/download your program. The best way to do this is with a 1747-UIC ( USB to DH485 converter). See links

If your computer has a real serial port you can use the 1747-PIC/AIC+ driver in RSLinx with your straight thru cable.

Or a memory card.
 
Last edited:
Since this is a company PC i really don't want to screw with it. I just want to pull the program out and save it. More info

The Panelview is plugged into a 1761-Net-AIC which is wire into a 1747-Aic. My processor is plugged into the CPU slot on the AIC & there is a DTAM plugged inti the RJ45 port on the AIC.
So if I don't modify the pc for the pic driver they will need to purchase a 1747-UIC--correct.

Thanks Mickey and All
 

Similar Topics

Got a problem on an install this weekend I'm hoping someone can help out on. I'm upgrading an old system with a SLC5/04 and Panelview 600...
Replies
3
Views
1,082
I have a PV600 (2711-B6C5) that has a single RS232 serial port that only talks (and apparently is restricted to) DH485. I have built my...
Replies
5
Views
6,408
I am trying to go to a 504 CPU. and on my hmi I am getting a 9028 error. can someone explain what they mean by change reference?
Replies
12
Views
192
Hi I have a number of the older PanelView Plus 600 HMI's (2711P-T6C20D, Ser D) that I want to update to the latest firmware. I believe that the...
Replies
10
Views
391
Hello, Friends Please someone help me find right cable to communicate Panelview 600 (2711-B6C9) to Micrologix 1200 (1762-L24AWAR). AND any advice.
Replies
3
Views
252
Back
Top Bottom