Hi All,
I need to be able to quote chapter and verse regarding e-stops. Specifically, the part that says something like, "E-stops shall remove all sources of energy from the machine (unless removal creates a more hazardous condition) and brings the machine to a stop as quickly as possible."

I remember reading this, but I can't for the life of me remember which standard it was in. I've checked NFPA 79, and didn't see it. I'm needing to remove both electrical and pneumatic power and I'm getting push-back from the uninformed. I need a cudgel to batter them about the head :)

Thanks!

-rpoet
 
NFPA 79 9.2.5.4.

It doesn't say that it has to remove all sources of energy. It does say that the category has to be determined by the risk assessment of the machine. Do a risk assessment and make your case.
 
NFPA 79 9.2.5.4.

It doesn't say that it has to remove all sources of energy. It does say that the category has to be determined by the risk assessment of the machine. Do a risk assessment and make your case.

Thanks, TConnolly. This is actually for a friend who's in a tough spot. This is what he needs. Thanks!


-rpoet
 
Remember Pneumatic / Hydraulic and Kinetic stored energy.
Also
the fact that Servo/VFD's can stop motors quicker when powered so you might tackle the safety differently in that case
 

Similar Topics

Hello, I have plc Schneider TM241CE40T with the hmi HMIS5T. Do you have idea how to disable a button after an emergency stop to vijeo designer ...
Replies
5
Views
1,445
Dear colleagues I am learning to program siemens plc. I have a problem with how to solve the problem with a power outage and emergency STOP...
Replies
3
Views
1,727
Hi, I would like some recommendations/advice on wiring of a dual channel Emergency Stop for a 240V AC motor (single phase), I have 3 options in...
Replies
47
Views
13,514
Hi, We have a machine that we wan't to restart after power on if the emergency stop is OK. But if the emergency stop is tripped with the button...
Replies
21
Views
6,478
I'm working on a project that has e-stop pull cords around the full length of a conveyor system which is about 750 feet long and it has 16 e-stop...
Replies
16
Views
7,981
Back
Top Bottom