lbric
Member
Hello,
i have a 1762-of4 connected to a ml1100. i setup an scp instruction with
n7:0
min 0
max 32760
scaled min 0
scaled max 10
output O:1.0
i know the analog card produces a 0 to 10v signal and want to use this to control the speed on a vfd.
when i run the program the output changes 0 to 10 but when i use my meter to check the output at vout0 and the common i dont get any voltage. the configuration for channel 0 is set to 0-10v raw/proportional. i took a look at the data table and i am only seeing the first 3 bits of O:1.0 change and according to the manual the output data should be on bits 3-14 but all these remain 0.
can someone provide some assistance, i wonder if my scp instruction is incorrect.
thanks,
Ricardo
i have a 1762-of4 connected to a ml1100. i setup an scp instruction with
n7:0
min 0
max 32760
scaled min 0
scaled max 10
output O:1.0
i know the analog card produces a 0 to 10v signal and want to use this to control the speed on a vfd.
when i run the program the output changes 0 to 10 but when i use my meter to check the output at vout0 and the common i dont get any voltage. the configuration for channel 0 is set to 0-10v raw/proportional. i took a look at the data table and i am only seeing the first 3 bits of O:1.0 change and according to the manual the output data should be on bits 3-14 but all these remain 0.
can someone provide some assistance, i wonder if my scp instruction is incorrect.
thanks,
Ricardo