Where is the contactor ?? on the supply or feed to motor.. Some VSD's don't like a motor open circuit and will trip as a result... Not familiar with the "micro driver" VSD, so the codes dont mean anything to me
Having not seen your installation, still sounds like it could be the fan....
Try winding out your ramp time a long way... I have been involved in a similar case where the sparky had decided the VSD was faulty, replaced it twice and finally put a DOL starter on it (which then caused the supply fuses to blow...)
Was all to do with the heavy fan blade on the end of the motor needing a lot of time for the motor to get it to speed. Was fixed by setting the ramp to around 90 seconds to 50 Hz, and spin stop to prevent regeneration issues on stop.. Ironically most pump / fan VSD's are light weight with overload ratings only slightly higher than nameplate...
Of course you may have a faulty VSD, or the motor could be wired wrong etc....