Hi JohnnySpark24
Bottom terminal strip of your MicroLogix
L1---L2---GRD---VAC OR VDC---O/0 VAC OR VDC---O/1 VAC--O/2--O/3
Think of your output as a relay inside the plc. The VAC/VDC connection
means it doesn`t care whether you are switching an AC or DC voltage through this set of contacts. VAC---| |---O/0 you access the coil of this relay with your program. Each terminal marked VAC/VDC, on your plc there are 4 means you could have this many different sources of control power. Input side there are two AC commons or neutrals so your 120 vac goes out to your device and comes back to an input.
Go to File choose New at this time you will choose a processor scroll down to MicroLogix 1000 and select it. You can name it or defalut is untitled. click OK here is a simple program. The first thing you do is insert a rung, then add the rest.
Forgive my lines between I:0/0 and O:0/0 this is the only way I can get them to stay in place, they don`t mean anything.
|
| Program
|---I:0/0 -----O:0/0
|----| |-------( )---
|--------------end
Save your program. Now open rslinks click Communications then configure drivers there will be a drop down list at the arrow choose
rs 232- DF1 devices as your driver. Have your pc hooked up to your plc and choose Auto config. This should let you talk to your plc.
Now in rslogix 500 there will be an arrow close to the top left side of your screen it will say Offline click this arrow and choose down load, then yes and yes. If all this worked now hook a neutral to AC COM on the input side of your plc and 120 volts to I:0/0 you will be online with your plc and can see it work.You don`t need anything hooked up to your out put contact for it to work. Rslogix 500 has excellent HELLLLLP files be sure and read them. You can learn a lot by reading the post on this site.
Good luck
Tom