365
I was studying Omron E5CN temp controller. I read in its manual that in order to drive a SSR, I have to use a temp controller with voltage output. (The control output can be relay, voltate, current types)
I always thought a SSR is used because of high on/off resolution. Then it requires digital output contacts (like PWM output) to drive the SSR. How does an analog output such as the voltage output drive an SSR?
Thanks.
 
SSR - solid state relay
some of these switch an output on with an input voltage
eg. 24Vdc - when you vary the input you can vary the output
- Analogue control
 
SSR - solid state relay
some of these switch an output on with an input voltage
eg. 24Vdc - when you vary the input you can vary the output
- Analogue control

I don't understand. So, when I control a 240V heater with a SSR, 24V input to the SSR produces higher voltage to the heater than 10V input to the SSR?
 
The voltage output on your controller is also known as a digital output. The voltage doesn't vary. It is either on or off, but it can be turned on and off very quickly. The solid state relay uses this logic signal to turn on its output(which equals the input), which in your case is 240VAC.
 
How SSR can be driven by analog?

Hello There, I am new with control system. I have a similar question. My application require to control an electric heater bank with a temperature controller. All the heater banks shall be modulated via new solid state relays in response to a 0 - 10 VDC analog control signal from the PLC. How can this be achived /posible. Kind Regards,
 
There are also companies that supply a circuit board device that you attach to a SSR in order for it t accept analog inuts to vary the output, similar to an SCR. HB Controls is a company that I have used these devices from and they work rather well. It comes with different options that can cover a wide range of applications.
 
You are probably talking about SCR's instead of SSR. SCR's can take an analog signal and use that to modulate the output.

That's the one I was talking about.
But.
It is a Solid State Relay. An SCR is a silicon Controlled Rectifier. Which is switched electronically.

To the OP
No you can not produce 240 from 24 Vdc
You need a 240 V supply as well
 

Similar Topics

Hello There, I am new with control system and electronic devices. My application require to control an electric heater bank with a temperature...
Replies
20
Views
7,389
Hello all... I'm looking for a 480v 3ø 25+ amp Solid State Relay to replace a mechanical one beating itself to death keeping temp in a heating...
Replies
15
Views
1,952
hopefully a dumb question. I'm doing a retrofit where a 120v switch is controlling a starter contactor. I'm adding PLC that uses a SSR (triac) to...
Replies
3
Views
1,417
Possibly a bit niche this one but does anybody know if there is an under/over voltage monitoring relay with an SSR or transistor signalling output...
Replies
3
Views
1,476
Inductive load: Vacuum Pump motor 115VAC 0.9Watts Resistive load: Heater 115VAC 0.75 Watts What is the best way to control these from...
Replies
6
Views
2,014
Back
Top Bottom