I am using a Direct 06 PLC with a F0-04THM card and a K type thermocouple. The card is in Slot 3. When I look at the V memory (v-2000) location after the programming, I see a number that might sometimes read 24E, 24C,24B, 24A, or 24F. Sometimes it read 249. The actual temp, according to the fluke analyzer is 50 degrees. The only thing the temp readout is for is for it to be displayed on a 6" DL HMI.
The card paperwork says it displays an actual temp with no scaling needed. So what am I doing wrong?

I am not sure how to write the logic here but I will do my best.

"SP0"---LD K0400"

"OUT V720"

"LDA O2000"

"OUT V721"

"LD K1"

"OUT V723"
"OUT V724"
"OUT V725"
"OUT V726"
 
View the results in 'decimal'. The reading is to the tenth of a degree the last digit being that 'tenth'. The decimal point is assumed.

24E = 590 (59.0)
24C = 588 (58.8)
24B = 587 (58.7)
24F = 591 (59.1)
24A = 586 (58.6)
 
That got it. Thanks. I have used GE plc's for years. Its seems as if there is a lot to learn with the DL's.

Thanks again.
 

Similar Topics

We've a diff output on a Siemens AO card. The card is a 6ES7 331-7TF00-0AB0 which has now been replaced by 6ES7 331-7TF01-0AB0. The...
Replies
2
Views
1,449
HI, Hopefully someone can point me in the right direction, the problem im having is with a direct logic 205 PLC DL260 CPU. The PLC in running a...
Replies
2
Views
4,146
Hey guys, I am currently working on a project involving an AD EA9-T6CL screen and a generic magnetic card reader. The purpose of the card reader...
Replies
6
Views
2,800
AUTOMATION DIRECT ANALOG CARD need to find out how to access status bits on analog card F4-08THM-J. Should have short circuit and burn out...
Replies
11
Views
3,103
This is a problem that recently arrived on a working machine. I am getting a constant 4095 (12 bit res)in my plc register from my analog card. I...
Replies
1
Views
4,195
Back
Top Bottom