Dear,

I have a control cabinet that send wireless signals to a remote system. this cabinet is powered from a solar panel. It is located in Dubai. do you think it needs lightning arrestors or surge protection for the wireless modem.
this cabinet is connected to solinst data logger which are already protected from surge.

http://www.solinst.com/Text/textprod/9100text.html

thanks!

charbel
 
Charbel, Whether or not you need lightning protection depends on the frequency of thunderstorms and lightning in that area. Also the cost of the equipment is a factor.

For expensive equipment, some lightning rods with large cables connecting to a good ground system may be cheaper than replacing the equipment after a large lightning strike. Strikes can produce a million volts and thousands of amps of current searching for the path of least resistance to the earth.

The best lightning protection system (overhead grids on poles are used in military ammunition manufacturing and storage) is one where the lighting current is intercepted before it hits the facility. If you use rods, route the cables away from your cabinet.
 
Last edited:

Similar Topics

I just asked tech support at Phoenix Contact a question and the answer is making me think maybe I have misunderstood relay ratings for years...
Replies
16
Views
2,857
I have a SC9-LS24-3 surge protection solenoid cable from automation direct...
Replies
9
Views
1,348
Hi Folks, Is surge protection recommended for field wiring connected to PLC inputs? For example, I/O originating from field devices located...
Replies
3
Views
1,166
by spec i must supply surge protection for each individual PLC input in my panel. These devices are all of the voltage free (dry contact type)...
Replies
11
Views
2,244
i've been told numerous time not to stack surge suppressors, but have never been told the reason why...?!? we have a project and there's...
Replies
34
Views
8,602
Back
Top Bottom