Load cell help

sharkyh2o

Member
Join Date
Dec 2013
Location
Snow Shoe
Posts
129
New to anilog signals. Using a 5-10vdc analog load cell not to exceed 15vdc straight to the input card on a micrologic 1400 processor and not getting the results i desire. At 10vdc each pound = 1. At 5vdc every 2 pounds = 1. At 15vdc each pound = 1.5, but i do not want to push the voltage limit. What would you recommend to be able to take the signal and be able to come within say .2 pounds
 
sharkyh2o,

welcome to the forum.

typically load cell outputs are in millivolts, not a 5-10 volt output. the specs usually say x volts per millivolt when using a load cell amplifier.

post the brand name and model number of the load cell and plc.

if it is as you say a 5-10 volt output, you will need to determine the exact output and do a scale (SCP) function.

regards,
james
 
The input can take up to 10 VDC. The circuitry is 12 bit A/D. This means the 10 volts is divided into 4095 segments. So, using the load cell at 10 volts, you will will have .0002 pound accuracy.

As James notes, most load cells have a very low voltage output and require an intermediate amplifier. Just out of curiosity can you provide a reference to data on this load cell?
 
Last edited:
i was expecting 4095 segments but i am not getting that. it is a 100 pound load cell and at 10vdc i am getting 0 at 0 pounds and 100 at 100 pounds. Sorry i am so vague, not at work now. I will get the specs tomorrow, just cant get this problem outta my head and i found this site. Learning as i go.
 
Does it go from a number of load cells to a summing board? They can be 10 volts at that point. As others have said a model number of the load cells and quantity.
George
 
a loadcell is 10milliVolt/Volt
with 10 volts on top and bottom the max is 100 millivolt, thus your input will not react.
you will need a amplifier, like a XTR115 or a industry unit.
 
Every load cell I've ever used is 2mv/v or 3mv/v. Never seen a 10mv/v.

a loadcell is 10milliVolt/Volt
with 10 volts on top and bottom the max is 100 millivolt, thus your input will not react.
you will need a amplifier, like a XTR115 or a industry unit.
 
gbeaker, the load cells you are familiar with use foil strain gages. Many of the load cells I use in the web handling industry use semiconductor strain gages. For example the CMC load cells we often use contain semiconductor strain gages that produce 20mV/V at rated load.

Keith
 
The loadcell needed an amplifier.I thought i could go straight to the input card with the loadcell signal.Working great at 5vdc and 1.6mv out. One more quick question, the lower the voltage the less chance of interfearance correct? Thank you everyone.



a loadcell is 10milliVolt/Volt
with 10 volts on top and bottom the max is 100 millivolt, thus your input will not react.
you will need a amplifier, like a XTR115 or a industry unit.
 
Originally posted by sharkyh2o:

One more quick question, the lower the voltage the less chance of interfearance correct?

For comparison's sake in any given application you can consider environmental noise to be a constant. That being said and all other things being equal, the larger your actual signal level relative to a given piece of "data" the less the "data" will be influenced by the noise in your environment. Basically the larger signal level provides a better Signal:Noise ratio.

I would say use the highest excitation the device is rated for.

Keith
 
sharkyh2o,

i have always used shielded cable for the load cell wiring with the drain wire going to the analog card com.

remember to tape the other end of the shield off or risk a feedback loop which induces noise.

regards,
james
 

Similar Topics

I have few questions regarding analog input. and i was wondering if you can direct me. i was able finally set my cards and connect my load cell...
Replies
3
Views
2,058
Hi everyone, so as i am still new to this. I will need help to confirm my connections load cell to my plc load cell will run on 10V max so that...
Replies
10
Views
2,480
New to anilog signals. Using a 5-10vdc analog load cell not to exceed 15vdc straight to the input card on a micrologic 1400 processor and not...
Replies
2
Views
1,751
I have to look into a new set up of a load cell fed into a HELM module (1769 series module with a Compactlogix). I spoke with HELM and gotten no...
Replies
2
Views
6,190
Dear All Friends I am trying to connect Siwarex U Load cell processor ( 2 Channel ) with Simatic S7 313 C CPU . But the SF ( System Failure )...
Replies
5
Views
5,693
Back
Top Bottom