Can someone confirm for me the adress structure for a Micrologix 1500 PLC.
The main base has 12 inputs and 12 outputs then slot 1 is 16 inputs and slot 2 is 16 outputs. Is the adressing for the base I:0/00 through I:0/11 for the inputs and O:0/00 through O:0/11 for the outputs. Then, is card 1 I:1/00 thru I:1/15 etc
Just want to confirm that the adress starts at 00 not 01 and that I have the base adressing right
 
From what I see is that the base I/O will be 0/x ie either I:0/11 or O:0/11 but the cards in the slot will be 1 and 2..ie slot 1 will be if input card I:1/0 thru 1/15 and slot 2 will be 2/0 thru 2/15. It displays it if you go into RSLogix and setup that processor with your cards, the I/O will automatically be set.
 

Similar Topics

I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
79
Hello, I have a 1764 1500 LSP Series A that keeps failing with DTL_E_FAIL I/O error. Searching around it seems there's a weird issue specifically...
Replies
2
Views
103
Good Day i Have Micrologix 1500 LSP, and I want to get data from plc and send it through Modbus RTU slave; I have only ch0 on that plc I Order...
Replies
6
Views
917
Hello folks, Hope everyone is doing fine. I got an OMRON NS10-TVOOB-V2 hmi screen last day and planning to use it with Micrologix 1500. 1. Is...
Replies
4
Views
1,206
Good morning to all, I need to modify an existing PLC MIcrologix 1500 configured with a Modem on Channel 1 (DF1 Full Duplex) and an...
Replies
7
Views
1,425
Back
Top Bottom