I have a compactlogix 1769-L32E, PV600+ and 3 Lenze drives (each drive fitted with a Ethernet IP module)
Both the compactlogix PLC and the pannelview+ are connected directly to a network switch and the drives are daisy chained together then connected to the switch with a single cable
when the system is as above everything works fine
But
I have to read data from another compactlogix 1756-L62 fitted with a 1756-1756-ENBT card (Version3.9)
So in my project i have added a connection for a 1756-ENTB/A module and added a MSG instruction (CIP Data table read) in the program
When the PLC is in run mode and the PLC that i read a data from is not on the network (i.e M/C switched off) then one of the drives (the one at the end of the daisy chain) has an intermittent comms timeout error, this error occurs every 5-15 mins
if the connection to the PLC that i read data from is inhibited then everything works fine.
I think this may be caused by RPI times, does anyone have any other opinions?
is there a common method to set/check RPI times as all are at default or am i missing something
Is there anything else i should be checking
Thanks in advance for any help
Andy
Both the compactlogix PLC and the pannelview+ are connected directly to a network switch and the drives are daisy chained together then connected to the switch with a single cable
when the system is as above everything works fine
But
I have to read data from another compactlogix 1756-L62 fitted with a 1756-1756-ENBT card (Version3.9)
So in my project i have added a connection for a 1756-ENTB/A module and added a MSG instruction (CIP Data table read) in the program
When the PLC is in run mode and the PLC that i read a data from is not on the network (i.e M/C switched off) then one of the drives (the one at the end of the daisy chain) has an intermittent comms timeout error, this error occurs every 5-15 mins
if the connection to the PLC that i read data from is inhibited then everything works fine.
I think this may be caused by RPI times, does anyone have any other opinions?
is there a common method to set/check RPI times as all are at default or am i missing something
Is there anything else i should be checking
Thanks in advance for any help