Hi, I am new. I have connected to a micrologix 1500 LRP series c. I can go on line, upload, download, but when I switch to run, it immediately faults out.

Help please!!
 
While online with the fault showing in the upper left click it and choose 'Goto Error'. This will present the status display. The reason for the error in on the right. Follow any documentation you have on resolving the error. For more help either report to us the complete text of the error or use a screen grab utility to capture a picture of the screen and post it here.
 
Last edited:
reply to 1500 fault

Fault routine S:29 [0 ]
Major error S:6 [52h ]

Error description

"The base minimum series selected in the user program configuration was greater than the series on the actual base."

Additionally a bit was set at: 'Major Error Halt' S:1/13
 
OK, you will have to inpect the lable on the Micrologix carefully. Then, in your project, double click on 'Controller Properties'. In 'Processor Type' click the arrow and find the processor which cooresponds to what you read on the lable. Save and re-try to download.

In addition you may need to verify the base and make sure it is properly entered under 'I/O Configuration' - select the CPU slot - 'Adv. Config.' - 'Embedded General Configuration (tab)' - 'Base/Type'
 
Last edited:
The quickest way to pull in the correct base type, series and revision is to do a 'Read I/O Config'.
You do this under I/O Configuration/Read I/O Config/Who Active.
Select (highlight) controller and then OK.
Then Read I/O Config again.
Then save the project and download.

Edit: Sorry didn't see your reply Bernie!
If a Read I/O Config does not get rid of the error for you then you should do as Bernie suggests and manually check/enter the data from the label. Note: The 'Series/Rev/Funtionality' should be set to the Revision of your controller, A in this case.

George
 
Last edited:

Similar Topics

Hi all, I am having an issue with a Micrologix 1500 1769-ECR. The PLC will not run and I’m unable to connect to diagnose the fault. When I power...
Replies
1
Views
2,456
We have a ML 1500 and it faults from time to time. The floor guys always clear it before I can get to it. Is there any way to see what caused the...
Replies
3
Views
1,699
We have on site 7 equal Micrologix PLC, controlling 7 equal HVAC system for 7 room. The room have redundant HVAC units. All of them have 2...
Replies
2
Views
2,482
I have a client with a Micrologix 1500 LRP processor that faulted. I had him send it to me so I could clear the fault. I plugged the processor...
Replies
11
Views
15,802
Hi, I came into work today and my co-worker had tried to do some electrical wiring in the panel where we have a Micrologix 1500 running. It was...
Replies
3
Views
2,991
Back
Top Bottom