Hi guys,
I have been asked to adjust the refresh time on a hsc and look at the scan time , I have found the refresh time but its greyed out online and offline? Any ideas how to adjust, all so how can I find the scan time, thanks stu
 
Stu is this a CompactLogix? If so you can't update the individual card you can only update the entire rack.
 
see if this helps ...

also - note that with the newer versions of RSLogix5000 (at least with version 20.01) you CAN set each local I/O module's RPI independently for COMPACT-Logix ...

but ...

reading between the lines, you seem to be having "I/O Update" issues on a high-speed application ... I suggest that you also read the following thread ... COMPACT-Logix has some nasty little tricks to play along these lines related to its Task Priority settings ... if this is indeed your problem, then setting up a faster RPI won't help you ...

http://forums.mrplc.com/index.php?showtopic=26162

TIP: play the "sound effects" file near the beginning of the first post ... if you think that something along these lines might be causing your problem, then consider posting your entire ACD file ...

.

cpx_set_compact_bus_rpi.jpg
 
Last edited:

Similar Topics

I am completely stuck on building a ladder program that requires a start button to be pressed 3 times to turn on motor 1. Then motor 2 starts...
Replies
20
Views
530
Hello Everyone, I have tried to access the help function from my RSLogix 5000 but everytime I select a function block on the PLC rung and press...
Replies
3
Views
1,270
I’m working with indirect addressing and trying to make an HMI where each Rectangle Object has a tag of “A[0-127]” with a correlating Push Button...
Replies
15
Views
4,198
I have been tasked to upgrade some SquareD PLCs at our plant. I have done several of these upgrades without any issues. However, I have now met my...
Replies
4
Views
2,440
Hi There, When i did FRD instruction in SLC 500 its working, when i try to simulate in RSLogix 5000 same way as i did in SLC 500 which is not...