jvargo Member J Join Date Jan 2014 Location Michigan Posts 2 Jan 30, 2014 #1 I'm having an issue setting up momentary push buttons. Everything else works fine, but the momentary button will not configure properly. When pushed it just flashes on and off rather than staying on when held. Any suggestions?
I'm having an issue setting up momentary push buttons. Everything else works fine, but the momentary button will not configure properly. When pushed it just flashes on and off rather than staying on when held. Any suggestions?
bernie_carlton Lifetime Supporting Member + Moderator Join Date Apr 2002 Location Yakima, Washington Posts 6,413 Jan 30, 2014 #2 See if the target bit is being turned off in the ladder program.
baldone Member B Join Date Feb 2011 Location Wisconsin Posts 205 Jan 30, 2014 #3 bernie_carlton said: See if the target bit is being turned off in the ladder program. Click to expand... +1....change the tag to an HMI tag and see if it works correctly. If it doe then something somewhere is turning off your target bit immediatly after you turn in on.
bernie_carlton said: See if the target bit is being turned off in the ladder program. Click to expand... +1....change the tag to an HMI tag and see if it works correctly. If it doe then something somewhere is turning off your target bit immediatly after you turn in on.
jvargo Member OP J Join Date Jan 2014 Location Michigan Posts 2 Jan 30, 2014 #4 solved This is a known issue with this unit. Must be directly connected to plc via serial connection. Rockwell not at all forthcoming on this one though.
solved This is a known issue with this unit. Must be directly connected to plc via serial connection. Rockwell not at all forthcoming on this one though.