I am experiencing a strange situation. The safety and instrument grounds are connected to separate earthing pits, the land has high moisture and salt contents, therefore the resistance between safety and instrument ground is 60 ohms approx.

The problem is when i connect multi-meter, it beeps when connected in one direction, if the multi-meter terminals are reversed there is NO beep.

Any suggestions, what might be causing this ???
 
Sorry to hijack this thread, but I've got a question about his comments at the end about the welder.

Our shops use large steel tables to do all their welding work. They always put the "Work" lead onto the table, and weld with the steel component sitting on the table.

We've always permanently bonded these tables to the steel structure of the building (which is also bonded back to the main distribution source). Is that still recommended? We've always been afraid that if the work piece lead became disconnected from the table that the welder might use the person as a path back to the source.
 
1.) Multi meter type?
a.) Earth Tester?
b.) Instrument Tester?
c.) Standard multi-meter?

2.) Standard multi-meter -> selection range kohm/ohm during “beep”?.
3.) The red probe on what side and black probe on what side during ”beep”.
4.) Recall the principle of diode + and - polarity . Test with diode with ur multimeter forward and reverse probe.result?
5.) Check/measuret instrument to ground with multi meter selection small range AC VOLT.
Any value?
6.) Safety Earth/Ground come from MAIN TRANSFORMER.
7.) Instrument Ground come from ???.
Nowdays earth and instrument already mess up,he,he.
 
5 stars for Milldrone's link
2ni8wf7.jpg
 
60 ohms is too high, to avoid ground loops, all grounds should be connected on 1 rail or bar anywhere.
And yes instrument ground should be possible to disconnect, to check for these ground loops.
The main ground wire should be same size as the feeding wires are (or 0.5 above thumbthickness(hihi)
with a multimeter it is impossible to measure as the voltage is too small to detect.
about 1 micro Amp is enough for the modern meters.
 
..the land has high moisture and salt contents, therefore the resistance between safety and instrument ground is 60 ohms approx.
For wet salty soil, you should be able to get 5 ohms or less between two separate grounding systems, IF you use concrete-encased electrodes installed according to the US National Electrical Code, Article 250.52.

A higher voltage on one grounding system relative to the 2nd one will cause a meter conductivity check to beep in one direction but not the other.
 
Last edited:

Similar Topics

After some interesting conversation regarding the safety of emergency stops, I saw some posts talking about the safety standard conversation...
Replies
17
Views
215
Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
Replies
1
Views
107
I'm struggling to get an FR-E800SCE to work on CC-Link IE TSN. I'm sure the issue is with the drive, when I plug in the network cable I get no...
Replies
1
Views
103
Hi I have a yaskawa gp7 robot arm which I am going to use for machine tending with a cnc mill. Is it a good idea to buy a SICK laser scanner for...
Replies
5
Views
234
Power flex 527 Network based safety drive had faulty and alarm pop up SOS Code internal fault Unable to set or clear the fault manually or...
Replies
5
Views
115
Back
Top Bottom