4-20ma---to split or not to splt

cjd1965

Lifetime Supporting Member
Join Date
Apr 2007
Location
UK
Posts
1,659
Hi
I have an existing device with a 2 wire pressure transmitter, 24V 4-20mA feeding a existing BMS device

I need to take that into a new separate PLC panel (Siemens S7 ET200s)

I want to split the signal but my boss wants to take the 4-20 into the ET200 and retransmit

The power supply at each panel is different

So,,opinions pls
 
I would think that you would want to use a splitter that has isolation since they are on separate power sources. Pretty sure we use a weidmuller brand... I can get a part # tomorrow.
 
Yes that what I was thinking...

Power the splitter from the new panel and bring exising 4-20 into it and feed the bms and PLC seperatly

My boss is thinking ET200 route is cheaper but because PSU are different it becomes more of a problem

Part# would be useful thanks
 
Try to put them in series as a lot of inputs are isolated from power supply, at least the ones i use (WAGO).
otherwise use a repeater with two outputs (best solution), this way the PLC can stop without problems on the BMS and other way around.
 
The separate power supplies shouldn't be a problem - I've done that before. Just make sure that neither input is tied to ground. If one is then you will need an isolator to avoid a ground loop.
 
I don't see and issue with just repeating the signal through the ET200. A splitter/isolator would be a more robust solution. Shooter's point about the PLC being able to stop without losing the signal downstream is definitely a valid one.
 
Hi All
I don't want to disrupt the existing installation or disconnect ground loops etc so have found a mA loop powered splitter from Status instruments which I can insert into the existing loop and then feed my PLC from that. Cheap too at approx. £100 each
 

Similar Topics

Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
Replies
5
Views
255
Problem: Our PLC can only output 4-20mA, but the actuators it needs to control, modulate based on a 0-135Ohm signal. Buying 4 or 8 individual...
Replies
7
Views
267
What's your go to 4-20ma isolator. I've got some 4 wire 4-20ma from several flow meters and scales that I would like to isolate before it gets to...
Replies
10
Views
1,679
Hi, I need to read three 4-20mA signals from a DCS(ABB) in a remote 6 channel analog input module with RS485 modbus port. When I connected...
Replies
2
Views
477
Hello this is my first post. Looking forward to being more involved in this community to learn and hopefully help others. Any help or guidance...
Replies
7
Views
776
Back
Top Bottom