bradal said:
...In the manual for the Compact 5370 Series it says that you must use two separate power supplies...Does it REALLY matter?...is this overkill?...
Why the need for two separate power supplies?...
475553 - CompactLogix 5370 L1 Power Connector
Access Level: Everyone
bradal,
Basically, the VDC+ and VDC- terminals only supply 24VDC to the embedded power supply, which powers the controller and its embedded I/O. It also provides 1A@5V to the POINTBus backplane, which only powers the modules. It does not provide a supply to the V and C terminals of either the embedded I/O, or the POINTBus modules.
The FP+ and FP- terminals are linked to these V and C terminals and provide the necessary field power. So it should be suitably rated to power all field I/O devices.
If you choose to connect a single supply to both sets of terminals, you may induce noise from the field back into the controller's internal system power lines. This could potentially play havoc with the POINTBus modules on the backplane. The fact the embedded power supply is non-isolated makes it susceptible to noise.
Ken Roach said:
The external 24V DC power source connected to the VDC+ and VDC terminals on the removable connector must reside in the same enclosure as the CompactLogix 5370 L1 controller.
Ken,
Again, this is to help eliminate noise on the wiring from the power supply to the controller by keeping the power supply and its wiring as short as possible a distance from the controller.
It's your call at the end of the day guys, but bear the noise issue in mind if you ever run into weird goings-on while using only one supply.
Some more info...
475558 - Calculating System Power Consumption on the CompactLogix 5370 L1 Controllers
Access Level: Everyone
493329 - Master Control Relay (MCR) wiring for CompactLogix 5370 L1 controllers
Access Level: Everyone
493835 - Embedded Input or Outputs not working on the 1769-L1ER?
Access Level: TechConnect
471241 - CompactLogix 5370 L1 Controller will not power up; stuck in a power up sequence
Access Level: TechConnect
George