I have a 1000 ohm 3 wire rtd going to a a.b. Rtd module using slc5oo software i'm thinking a scp is best to scale it and then display on a panelview, but i don't know what the input min/max and scaled min/max would be? Or is there a better way to do it? Thanks
 
SLC RTD cards can give you temperature values directly depending on how you have the card configured. (Engineering Unit X 1 or Engineering Units X 10)

What card are you using? Complete catalog number.
 
See picture below for raw data values depending on how you have your card configured.

As you can see if you use "Engineering Units X 10" you will get temperature directly no decimal. If you use "Engineering Units X 1" you will get temperature with an implied decimal point. Use math instruction to move the decimal point.

If you use any of the other raw data formats then a "SCP" instruction will do the scaling to get engineering units for you. See picture for engineering unit range for your 1000 ohm RTD.

Rawdatavalues.png
 

Similar Topics

Good day all. I would like to know if anyone might know why the Control Logix RTD modules do not require a drain wire (shield) connected to it...
Replies
8
Views
3,417
Good day all. I have a SLC5/03 with a 1746-NR4 RTD Module. I'm using 100-Ohm RTD's in acid baths. When the calibration tech measured the tanks...
Replies
31
Views
6,902
Good day all, I changed the configuration of an RTD Module and when I resumed the program the system had a fault and shut-down. The module is a...
Replies
11
Views
4,741
Good day all. I have an RTD module for a SLC500 5/03 that I can't get the temperature values to stop jumping from one temp to the next, on the HMI...
Replies
16
Views
4,647
Hello all. I have two RTD's in the same acid tank. One reads 104 degrees F and the second is reading 54 degrees F. They are both at the same level...
Replies
4
Views
1,938
Back
Top Bottom