Inview dh485 module

yojunib

Member
Join Date
Nov 2013
Location
kerala
Posts
25
I need InView P22R to be communicated through DH485 communication module. I have programmed the inview and also in PLC (PLC 5/40) , but i am unable to download the communication configuration to the DH 485 module.

The DH485 communication module that i have is " INVIEW DH485 MODULE" Cat No: 2706-PDH485P.

I tried downloading the configuration to DH 485 module through serial communication.
Default settings
COM 1;
Cable used is : 2711-NC13

Downloading screen appears but it is unable to identify the operating terminal.

Can u tell me how u configure the Invew DH485 communication module.

I also have a Invew RIO module how to download the communication settings to it.
 
Last edited:
The 2711-NC13 cable is not correct for downloading to the module:

Download Cables
InView Communication Module Standard Type Cable to Personal Computer
DH-485 Comm Port only or DH-485 Comm Port and RS-232 Port 1747-PIC

DeviceNet Comm Port and RS-232 Port
ControlNet Comm Port and RS-232 Port
Remote I/O Comm Port and RS-232 Port
Ethernet Comm Port and RS-232 Port
DH+ Comm Port and RS-232 Port
all use the 2711-NC13 (5 m/16 ft) -OR- 2711-NC14 (10 m/32 ft) -OR- 2706-NC13 (3 m/10 ft)

Check the manual page 26 http://literature.rockwellautomation.com/idc/groups/literature/documents/um/2706-um017_-en-p.pdf
 
The 2711-NC13 cable is not correct for downloading to the module:

Download Cables
InView Communication Module Standard Type Cable to Personal Computer
DH-485 Comm Port only or DH-485 Comm Port and RS-232 Port 1747-PIC

DeviceNet Comm Port and RS-232 Port
ControlNet Comm Port and RS-232 Port
Remote I/O Comm Port and RS-232 Port
Ethernet Comm Port and RS-232 Port
DH+ Comm Port and RS-232 Port
all use the 2711-NC13 (5 m/16 ft) -OR- 2711-NC14 (10 m/32 ft) -OR- 2706-NC13 (3 m/10 ft)

Check the manual page 26 http://literature.rockwellautomation.com/idc/groups/literature/documents/um/2706-um017_-en-p.pdf
Can u please tell me how to download program to INVIEW DH 485 comm module.

In Manual it says that "The DH485 communication module requires you to download
the application over the DH485 network. You cannot download
over the RS232 port on a DH485 communication module"

How to do that with out RS-232 Port 1747-PIC cable
 
Last edited:
Page 37 of the manual says:
Connect a Computer
On InView DH-485 communication modules, applications are
transferred:

-- through the DH-485 programming connector to the InView communication module.
- •through any node on a DH-485 network.

To connect a computer to the InView communication module, you need:


a cable (same cables used to transfer applications from APS software to SLC)

0.3 m (1 ft) cable, catalog no. 1747-C11
1.83 m (6 ft) cable, catalog no. 1747-C10
6.1 m (20 ft) cable, catalog no. 1747-C20

Personal Computer Interface Converter (PIC), catalog no.

1747-PIC. The PIC connects to the computer. The cable connects the PIC to the DH-485 programming connector.

 

Similar Topics

I have an InView P22R with the external 2706-PDH485P comm module. The module requires external +24VDC to operate. It is configured (programmed)...
Replies
2
Views
1,576
Hello Friends We have a Inview 2706-P72CN2, it had been working OK. Showing OK Parts, NOK Parts and Goal Parts. Suddenly, it has stopped working...
Replies
0
Views
330
Hi, I bought a Weinview/Weintek MT8071ip HMI and an EasyAccess Activation Card. I have activated the card on the HMI (it says activated), but...
Replies
1
Views
901
Currently I'm programming a Controls Spectrum InView P42C-SC using a ControlLogix. The display has an ethernet communications module attached to...
Replies
1
Views
1,338
I have a customer that sent me the email below, I have been trying to find an answers in the manuals but cant find much to help He is using a...
Replies
3
Views
4,384
Back
Top Bottom