Dear,

There are requirements that requires to have junction box in fuel hydrant valve chamber, the multicore / multipair cable getting out of the junction box will be connected to the instrumentation cabinet (which contains remote I/O's) which is located in an electrical chamber.
Both the hydrant valve chamber and the electrical chamber are located below ground level.
Zener barrier is located in the non-hazardous area protecting any electrical spark from the non-hazardous area to occur in the hazardous area.

Technically, is this required to have a junction box (which allows for easy connection of spare instruments) or cables can be layed directly going from the field instruments to the instrument cabinet. From comon practice, is this usual the case, not using junction boxes?

thank you for your feedbacks,

charbel
 
dear shooter,

you are definitely right, but is it required to have junction box in the valve chamber as stated below?

thanks!

charbel
 
thank you shooter,

What is in your opinion any way to allow for spares in the chamber, what if laying a empty conduit from the hazardous area to the non-hazardous area, this conduit should be capped (in a way...)and allow for the allocation of future spares.
 

Similar Topics

i am new to these things. I have no intention of using this in a commercial way whatsoever. I wanted to write a small plc programme for myself. We...
Replies
18
Views
7,845
Hi! We currently have a junction box and everything works fine, but one thing just bothers me and that is how I handle the cablescreen for the...
Replies
3
Views
1,358
Hi all, which terminals are you using for continuing shields in junction boxes without earthing them?
Replies
3
Views
4,667
Unfortunately we have problem with our newly purchased machine from a remote manufacturer. The prob is the water getting inside the junction...
Replies
4
Views
2,532
Hi all, Recently, I had to segregate a large enclosure between AC and DC and interlock the AC Doors. I started thinking should this be applied to...
Replies
10
Views
2,228
Back
Top Bottom