I need to measure temperature stratification in a large tank. I'm looking for a sensor ~20 feet long that can measure temperature at points every few feet?

Anyone used anything like this?
 
I've never seen such a critter. I'd suggest taking a 20' length of reasonable diameter pipe, weld nipples at the required increments, and thread thermowells with RTDs onto each. You could then run the wiring up through the pipe. The thermowells would permit acces to the RTDS for replacement, testing, etc.

Make sure you put wire numbers on each lead before you install the RTDs - otherwise you have a lot of ringing out to do!
 
Google 'multi point RTD'

Burns Engineering makes them, as do others. They're used for exactly what you're doing, temp gradients in tanks.

http://www.burnsengineering.com/document/pdf/Averaging-Multipoint_Measurement_Compendium.pdf

Good info - often come across needs for something like this.

Upsides : Most people just put multiple stabbings in the side of the vessel for thermowells. But that can be a PITA if the vessel has heating/cooling jackets / insulation etc.

Downsides : if one of the sensors fails, you have to replace the whole shebang, which would obviously be higher cost. It might also need a roof removal or "maintenance aperture" - getting a 20+ foot probe out of the top of a 20+ foot tank would need a lot of room "up there".

Generally, I would say that if a temperature gradient in your vessel is a problem, rather than a process requirement, then it's time to install a mixer, or a rousing loop.
 
Multipoint sensors are used extensively in the refined petrochemical markets because the storage tanks are huge, the gradients exist and the density/temperature relationship contributes significantly to the (in)accuracy of the tank volume calculation.
 
Multipoint sensors are used extensively in the refined petrochemical markets because the storage tanks are huge, the gradients exist and the density/temperature relationship contributes significantly to the (in)accuracy of the tank volume calculation.

Mostly "outside", I guess...

But as I said, good info, and nice to know they can be made to order
 
several options here, put them on the outside, simple under a bolt on each height.

another one use a big pipe, and a smaller hose, mount the sensors on the smaller one, with centre rings to keep it in place.

cabling should be taken care off, with Pt100 best use 4 wires/sensor, 3 is also possible, even 2 is possible with a gnd wire going to each sensor.
as speed is very low you can use a switcher.
another one could be together with the level sensor on a float that sinks (used in marine to see the temperatures in the big ocean)

still another one is optical fibre, it is more expensive as a simple sensor but the results are very good.
 
Since this answer was so easy for y'all, perhaps you all know where to find an inexpensive MUX for all the RTD's?
I ran across one that cycles through 4 channels and provides 4-20 output. 2 digital outputs provide the PLC feedbacl on which channel is being read.
Thats a good solution but I need at least 6 channels.
Since these are so expensive, I want to build the first one of these as a proof of concept so I'll grab a bunch of RTD's but I still need a mux. Ideas?
 
What plc? I would look at a remote rack or a small brick plc.
I an an AB guy so I would use a small MicroLogix1400 with 3 Spectrum controls 1762sc-IF8u. 8 thermocouples or 4 RTD. I think they are $400 a card so under 2k you have the PLC ready.
 
(Wow, its been a year ? )
This has been put back on radar to do before summer starts. I like the modules from Spectrum. That looks like a good direction to go.
 

Similar Topics

I'm fairly new to Rockwell software, I've had some basic training in the past but nothing too advanced. My company and I use Reliable products for...
Replies
9
Views
164
Hi all, I am having issues accessing my Cimplicity software - the site code changed after re-install and I am no longer able to attain a new key...
Replies
10
Views
135
Good day all! Can someone help me with the procedure to update Beijers E700 firmware? The Panel I am working on is firmware 2.04v and I would...
Replies
1
Views
56
Good evening. I display the step number of a SFC on a display. Sometimes, on a trip, it goes quickly through many steps and I need to prove to...
Replies
1
Views
113
Good morning all. I'm working on a rehab where they had a standalone InTouch 2014 HMI that they called a SCADA, but it's really basic stuff. The...
Replies
4
Views
172
Back
Top Bottom